| Basically it's a 60 amp 3-phase circuit that feeds your dimming system. The breakers are tied together so that if one trips, they all trip preventing potential damage to the equipment should it still attempt to operate on one or two legs. Also, it ensures that you have disconnected ALL of the power feeding the lighting system if you ever have to turn it off. There is no better way to ensure that you hit the correct breakers.
__________________ - AVOID VIDEO THEFT! Convert over to Betamax! |
| ||||
| Quote:
So for instance, you could have as many as 8 breakers and dimmers behind a 60A circuit but it's not likely that you have a 160A load.
__________________ - AVOID VIDEO THEFT! Convert over to Betamax! |
| |||
| Quote:
(gets out code book and calculator) |
| |||
| The key question is - what is the Connected Load? The amount of load demand should not exceed either a) the capacity of an individual dimmer and b) the total demand from all dimmers should not exceed the capacity of the feeder circuit breaker. How you divide it up does not make too much difference with theatrical lighting where the levels keep changing. If you are planning to have everything at full for very long, then it would be a good idea to balance the loads on each phase. But, with small shoebox dimmers, you do not have too much control over which phase is loaded. SteveV |
| ||||
| In our current setup we have 3 8-channel rack-mounted dimmer packs running off of 80A breakers on a 200A 3-phase service panel. If you do the math, you will see that we are technically way over capacity. But we are well within compliance of the code because if 3 or more circuits on the same leg pull 80 amps at the same time, it will trip the main breaker.
__________________ - AVOID VIDEO THEFT! Convert over to Betamax! |