Originally Posted by technerd View Post
...Amp racks hidden in the back of stages are forever wired on different phases from the front of house gear. You can loose some members that way!
I'll agree with most everything except this. Good electrical distribution practice divides loads -- especially heavy loads -- equally among the three phases, because this minimizes neutral currents at the service equipment (i.e., breaker panel) and therefore minimizes the voltage potential between neutral and ground. In a larger system with multiple power amps, it's quite common to find the amps purposefully fed from different legs of the three-phase from the same breaker panel.

So long as your AC is wired according to code, phase has nothing to do with safety. In the worst case, even if you have a backstage amp powered from one leg from one breaker panel, and a stage outlet running on a different leg from a different breaker panel, you might have problems with hum... but it still won't be a safety issue.

-- Jeff
Reply With Quote Start a New Topic From This Comment
  #38 (permalink)  
Old Friday, November 20th, 2009, 11:55 AM
waynehoskins's Avatar
The Crazy Analog Guy
Become a CMN Professional Member!

 
 Join Date: May 2006 
 Last Online: Today 
Quote:
Originally Posted by DTV-Engineer View Post
I'll agree with most everything except this. Good electrical distribution practice divides loads -- especially heavy loads -- equally among the three phases, because this minimizes neutral currents at the service equipment (i.e., breaker panel) and therefore minimizes the voltage potential between neutral and ground. In a larger system with multiple power amps, it's quite common to find the amps purposefully fed from different legs of the three-phase from the same breaker panel.

So long as your AC is wired according to code, phase has nothing to do with safety. In the worst case, even if you have a backstage amp powered from one leg from one breaker panel, and a stage outlet running on a different leg from a different breaker panel, you might have problems with hum... but it still won't be a safety issue.

-- Jeff
In fact, my amp rack at the church is purposefully balanced across three phases. Absolutely no hum problems resulting from that. In large installs, that's pretty much the norm, to balance the load on the trafo. Or in a stadium gig, to balance the genny.
Reply With Quote Start a New Topic From This Comment
Reply

  The Church Media Community > Audio > General Audio

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:



Add to Google


Register Now for FREE!
Our records show you have not yet registered to our community. To sign up for your FREE account INSTANTLY fill out the form below!

Username: Password: Confirm Password: E-Mail: Confirm E-Mail:
Agree to forum rules 


All times are GMT -6. The time now is 11:34 PM.

   
 
© 1995-2008, ChurchMedia™, ChurchMedia LLC

SEO by vBSEO 3.1.0